Quote:
In my wasted little brain I figure the cords to the lamps are only 18/2 thats pretty much standard from sunlight supply anyway, My question to all you wizzards out there, is 277 vac enough?
If you will look closely at your lamps cord, it should say somewhere on it what type of cord it is. The industry standard is either SO or STO cord. This is a reference to the cord insulation standards. SO and STO cords are rated for 600 volts and 18 gauge has a max ampacity of 10 amps. The NEC code standard most everyone uses as a universal ampacity reference for wiring is specific to THHN and should not be used as a one size fits all standard.
Quote:
okay have you ever heard of a "hot start?" This is when voltage is applied immediatly not letting the pressure build in the bulb first, this is what the capacitor charge time is for. Yes, you can run a 1 cap and 1 igniter for both bulb, but you are also going to be going through bulbs left and right and your lumens rate will wear down very quickly.
Your understanding and use of the term "hot start" is completley wrong. As kushman tried to explain. the proper term is "Hot Restrike" and refers to trying to relight the arc in a HOT hid lamp. When ever the lamp is hot, more precisely when ever the arc tube is hot, the gas pressures inside it are higher. Because of the higher pressure, the voltage needed to get the arc to jump the gap between the electrodes is higher. Ballasts are only capable of supplying a very narrow range of voltage to the lamp, therefore you have to let the lamp cool enough to get the pressure down enough so the voltage needed is within the range supplied by the ballast. It has absolutely NOTHING to do with capacitor charge time.