quick electrical question. please help
so today i called the department of water and power to turn on the power for my new place, but since it zoned in the business side they asked a shit load of question. long sorry short the guy on the phone was asking me what i would be running, i didnt want to tell him i would be running 4 x 1000w lights to grow herb duh. so the quickest thing that came to mind i said i was having a 2 or 3 ton a/c installed. he quickly said that would be to much power as i only have a 110v 1 phase meter. he said i would need a 3 phase.
actual equipment i would be running would be
4 x1000w with a titan or cap controller
24,000 btu split a/c for flower
12,000 portable a/c for veg and living space
600w mh
a couple of can fans
and wall mount fans
so for those of you who understand what the guy said on the phone, can you please tell me in stoner terminology.
will i be able to run this equipment?
is this an easy fix my electrician can do?
quick electrical question. please help
are you sure he said 110 volt? The normal minimum electrical service for a residence would be 100 amp 240 volt, if it was installed in the last 40 years. That would let you run your total load of approximately 70 amps. at 240 volts. If you actually only have a two wire 110 volt service and it would need a 200 amps, and I've NEVER seen such an installation.
quick electrical question. please help
The company man was only right.
And no, it's not something your local electrician can "fix".
However, If your grow is not installed yet, the power company can probably upgrade your sevice.
Ask him what it might cost.
Weeze
quick electrical question. please help
Quote:
Originally Posted by Weezard
The company man was only right.
And no, it's not something your local electrician can "fix".
However, If your grow is not installed yet, the power company can probably upgrade your sevice.
Ask him what it might cost.
Weeze
awww you just made me a sad man .... i guess i could let them come but when i asked if they can come change it the guy said it could take months . and i cant wait that long for my medicine
quick electrical question. please help
im pretty sure ill post some pics in like 10 min
quick electrical question. please help
Quote:
Originally Posted by kreator34
im pretty sure ill post some pics in like 10 min
here are the pics i took Attachment 292747Attachment 292748Attachment 292749Attachment 292750
the 3rd pic you see is what seems to be where my power is coming from out side my next door neighbor has one but i dont think he uses it cuz in that 4th pic the another box he has i dont know what is for i didnt want to get to close and make it seem like i was snopping around cuz the tenant before me said hes pretty sure they grow which i dont care duh better for me people mind there own business
quick electrical question. please help
the first 2 pictures are a 240V breaker box.
The main breakers look like 100 amp service with 6. 20 amp circuits.
The third picture is a 110v single phase ancient POC.
If it's yours, you do not want to grow there.
The 4th is a phone terminal box.
Sorry fo' makin' you sad brah, but I calls 'em da way I sees 'em. :)
Aloha,
W. IBEW
quick electrical question. please help
Quote:
Originally Posted by Weezard
the first 2 pictures are a 240V breaker box.
The main breakers look like 100 amp service with 6. 20 amp circuits.
The third picture is a 110v single phase ancient POC.
If it's yours, you do not want to grow there.
The 4th is a phone terminal box.
Sorry fo' makin' you sad brah, but I calls 'em da way I sees 'em. :)
Aloha,
W. IBEW
its okay i just didnt want to here bad news, sometimes you have to call them like you see them.
i know you said if its mine i dont want to grow in there but i got no other choice chef. i already signed the lease, my dumb ass thought if i just had someone install a cap 8 or titan i would be fine ... FUCK .... whats my next option?
quick electrical question. please help
Quote:
Originally Posted by Weezard
the first 2 pictures are a 240V breaker box.
The main breakers look like 100 amp service with 6. 20 amp circuits.
The third picture is a 110v single phase ancient POC.
If it's yours, you do not want to grow there.
The 4th is a phone terminal box.
Sorry fo' makin' you sad brah, but I calls 'em da way I sees 'em. :)
Aloha,
W. IBEW
oh i forgot to mention this other electrical shit is in side but the last tenant that was here said all this other shit is not even connected , but i was wondering if it will help
Attachment 292751Attachment 292752
quick electrical question. please help
so, this is 'your new place'. What is it, exactly? An office space? I can't make much from the photos and your descriptions. It's hard to say if you have enough to do a grow. If indeed all you have is the fuse box in the third photo then you got nothing to work with
Shov
IBEW - retired